Electrical grid description from c.s.y2k
From: Fred Swirbul Newsgroups: comp.software.year-2000 Subject: Y2K Induced Electric Grid Failures Date: Mon, 06 Apr 1998 05:33:51 GMT
Lets say Y2K hits. Lets be optimistic and say only a few large electric generating units trip. Most of us will still have power, right? Maybe not, and here is why.
(The following example is based on the US Western Grid. It is comprised of about 12 states in the western most continental US, from California to Wyoming, Washington state to New Mexico. This interconnected grid is "controlled" by the WSCC (Western States Coordinating Council). The events postulated below are similar to the August 1996 event that caused power outages for somewhere in the neighborhood of 25-50% (rough guess, I don't have the exact number) of the population of those 12 states, typically for a number of hours)
First, a few basics on large scale electric power generation and transmission.
1) Power generated must always equal power consumed. If it doesn't, grid disturbances start to occur. Some may be minor, as when a car on cruise control hits a small hill. The cruise control automatically kicks in more gas, and you regain your crusing speed. The same thing occurs automatically with electric power managment systems. Some may be larger, as when your car hits a big hill. Typically you want to take it out of cruise and control it manually. Manual operations like this occur on the grid, by starting peaking units (small, rapidly started electric generation units), or controlling it in other ways (I will skip the really technical stuff). If you run your car into a wall, your air bag inflates to hopefully save your life, so you can drive another day. If the grid is run into a wall, it also has automatic protection systems (circuit breakers, sort of like in your houme, but much bigger), to protect the electric generation equipment (to make power another day), but puts you in the dark for right now.
2) The primary purpose of connecting many electric generating units together (as seen on the western US grid, and many other places), is to provide a higher level of reliability, over all (it also makes it easier to buy and sell power amoung utilities and others, but that is a whole different topic). If one generating unit trips, the great multitude of others can typically and easily pick up the load, and everyones lights stay on. If each electric utility was its own "island", even one large plant tripping would probably put everyone in that area in the dark.
So how can only a few large electric generating units tripping off line cause a large disturbance on the electric grid (making it seem like it "ran into a wall")?
In the US western grid, the primary reason goes back to the fact that some areas are net producers of power, and some are net users. Washington State and Oregon produce a lot of excess power, primarily hydro-electric. California needs the power (and pays good money for it). There is a very large transmission line from the northwest to California, that is often at peak capacity, especially in the summer. Lets say a few generating plants on the southern part of the grid trip. You might only initially lose 4 Gigawatts (four big plants) out of the about 100 Gigawatts (again rough number), of power produced on the western grid. Other plants in other areas try to pick up the excess load, including the plants that are on the far side of that major north-south transmission line. Since it is already loaded at near peak, the protective equipment to those lines will open, protecting the equipment (good), but worsening the grid disturbance (bad). Power might try to continue to flow from north to south via other transmission lines (remember, the northwest is a net power producer, and Californai is a net power user). These lines can't handle that much power either, and their breakers open. You might be left with the western grid split into two or three large islands.
But the problem doesn't stop there. All areas are still in the middle of a grid disturbance. This grid disturbance can cause other plants to trip while protecting their own equipment from this very disturbance. Also, remember, power generated must always equal power consumed. The northwest is producing more power than is needed, the southwest is producing less. Because this is a fast acting event (just a few minutes once the big generators trip), human intervention is too slow to help. Generating units trip off and/or loads (like your home or business) are shed until power generated roughly equals power consumed. This might stabilize at about 50% of where things started at (i.e the lights are out for only half the people).
When an eletrical generating unit trips, it could take hours to days to get it producing power again, assuming no Y2K problems.
Obviously, the electric utilities know about this problem (at least the responsible people in my utility do). However, there are no operational strategies in place yet for the entire western grid to attempt to counter this type of problem. A single utility typically can not unilaterally decide to isolate themselves, because of open access laws, and because of contractual agreements for the power they produce. Of course since it is only a strategy that needs to be put in place, time is available to make things better. Unfortunately, since no one knows how many generators will trip off line due to Y2K, it makes it much tougher to plan for contingencies.
Hope this helps.
As always - I don't represent my emplower.
Fred Swirbul |