[HVAC] Discussions about HVAC, Elevators etc at the WTC
To me it seems the elevators at the WTC are no problem. Here is a description of the systems controlling the HVAC in the WTC etc. Lots of computerisation; so they will be doing quite some testing.
Technical but interesting.
John ________
'RonKenyon <ronkenyon@aol.com> wrote in article <1998051522265200.SAA04238@ladder01.news.aol.com>... > Stephen Poley wrote: > >>>I know it's a little off the topic you were actually discussing, but I > >>>can give one concrete example. The lifts in the passenger terminal at > >>>Amsterdam airport > < ... > > > Did anyone ever track down make-or-break details on the reported NY World Trade > Center elevator test? Harlan? > -- RonKenyon
Here's some of the correspondence:
-----Original Message----- From: Harlan Smith [SMTP:hwsmith.XOUT@cris.com] Sent: Saturday, April 11, 1998 3:05 PM To: 'berengaria.winkler.XOUT@nordstrom.com' Subject: WTC Elevator Story doesn't check out, so far
Berengaria,
[snip] Although I do not have a written review of the test conducted at the World Trade Center, the test example was presented at a recent Year 2000 forum that my manager and I attended. Recently the facilities and operations group at the World Trade Center, ran year 2000 tests on 2 of their main elevators. They rolled the internal clock, the elevator went up, came down and turned itself off. When they went back into the system to turn the clock back to present time, the embedded chip would not take. What was supposed to be a 2 hour test, turned into a lengthy night run to remove the embedded chip, find a replacement and set the new embedded chip before the work day began. For clarity and details about the test procedures that they used, I would advise contacting the World Trade Center directly.
I have found in my research as project analyst for this project, that the IEEE professional organization has not taken the opportunity to take the stage on the embedded system and year 2000 issue. I am quite surprized, as their English counterpart, the IEE in England, has posted on their web site and is selling a recent publication on the very topic. I have ordered the publication, and it has proved to be very useful, as my colleagues in facilities and operations were looking for this very material. I would advise visiting the IEE web site: www.iee.org.uk. - BW [end snip]
We have contacted WTC and they say that the incident did not occur and that they are just now commencing Y2K testing.
Also, there are supposed to be 275 Otis elevators in the WTC and Otis claims complete compliance.
Now they do have a big control system strapped on the WTC and I rather suspect it does have problems.
Can you please identify the specific conference and also the speaker who related this tale?
Harlan Smith
-----Original Message----- From: berengaria.winkler.XOUT@nordstrom.com Sent: Thursday, April 16, 1998 7:25 PM To: hwsmith.XOUT@cris.com Subject: RE: Elevator Test Example - Resource
Mr. Smith: I apologize for not getting back to you earlier this week; I have been out of town and subsequently catching up with pressing items. I have, in addition to your inquiry, received another question about this very facility test that I heard about at a conference presentation. As I stated in my initial note at the on-line conference, the information regarding the World Trade Center Tower elevator test, was presented as an example at a conference I attended here in Seattle. Please note, I encourage direct inquiry to the facility and elevator manufacturer, but for clarification, that I should have stated in my initial message, I received this information at the Gartner Group Strategic Forum, "Year 2000: The Landscape is Changing!" - presented by John Bace of the Gartner Group. In the meeting materials, the following number is given for inquiries to the Gartner Group Year 2000 client service, (203)316-1255. You may be able to directly inquire via this number. We have not as yet tested any of our elevators, but may conduct such tests -pending the inquiry completion we have with our vendors. If there is any other information and resources that I may provide, please feel free to contact me. Thank you , and I hope that this has been helpful as well as providing some clarification. Berengaria Berengaria Winkler NORDSTROM Year 2000 Project Office (206)233-5718 Fax: (206)233-6352 Tie Line: 8-891-5718
> -----Original Message----- > From: Harlan Smith [SMTP:hwsmith@cris.com] > Sent: Saturday, April 11, 1998 1:05 PM > To: 'berengaria.winkler.XOUT@nordstrom.com' > Subject: WTC Elevator Story doesn't check out, so far > > Berengaria, > > [snip] > Although I do not have a written review of the test conducted at the > World > Trade Center, the test example was presented at a recent Year 2000 > forum > that my manager and I attended. Recently the facilities and operations > > group at the World Trade Center, ran year 2000 tests on 2 of their > main > elevators. They rolled the internal clock, the elevator went up, came > down > and turned itself off. When they went back into the system to turn the > > clock back to present time, the embedded chip would not take. What was > > supposed to be a 2 hour test, turned into a lengthy night run to > remove the > embedded chip, find a replacement and set the new embedded chip before > the > work day began. For clarity and details about the test procedures that > they > used, I would advise contacting the World Trade Center directly. > > I have found in my research as project analyst for this project, that > the > IEEE professional organization has not taken the opportunity to take > the > stage on the embedded system and year 2000 issue. I am quite > surprized, as > their English counterpart, the IEE in England, has posted on their web > site > and is selling a recent publication on the very topic. I have ordered > the > publication, and it has proved to be very useful, as my colleagues in > facilities and operations were looking for this very material. I would > > advise visiting the IEE web site: www.iee.org.uk. - BW > [end snip] > > We have contacted WTC and they say that the indcident did not occur > and > that they are just now commencing Y2K testing. > > Also, there are supposed to be 275 Otis elevators in the WTC and Otis > claims complete compliance. > > Now they do have a big control system strapped on the WTC and I rather > > suspect it does have problems. > > Can you please identify the specific conference and also the speaker > who > related this tale? > > Harlan Smith Subject: Re: OTIS Elevator and Y2K From: "Harlan Smith" <hwsmith.nowhere@cris.com> Date: 1998/04/10 Message-ID: <01bd649b$097f7b60$46969bcf@CRC3.concentric.net> Newsgroups: comp.software.year-2000,comp.arch.embedded [More Headers] [Subscribe to comp.software.year-2000]
Here's some more on WTC
hsq.com
[snip] HSQ Technology Delivers Operations Control Center to World Trade Center
In May of 1997, HSQ Technology delivered a Building Management and Supervisory Control and Data Acquisition System (SCADA) to the Port Authority of New York and New Jersey for the World Trade Center (WTC) in New York City.
HSQ's MISER SCADA software and hardware package is located in the Operations and Control Center (OCC) of the WTC and functions as a complete Building Management System (BMS), coordinating the operations of the other building control and monitoring subsystems.
The World Trade Center is a very large complex of five buildings consisting of two 110 story towers (including 6 sub-grade levels each), two 10 story buildings, and the Concourse. The towers and Concourse portion of the Center were completed in 1973. Each tower is 1,350 feet (410 meters) tall, second in height only to Chicago's Sears Tower.
Design Criteria
In March of 1996, the Port Authority issued a Request for Proposal (RFP) for the design and implementation of the OCC/BMS project. In the RFP, the NYNJPA set four main goals:
Provide a central command center to improve the performance and monitoring of all base building and emergency systems. Provide areas from which to coordinate emergency response activities. Ensure that no single event would impair communications, control and monitoring functions. Provide flexibility for future adaptation to new technology and growth.
HSQ's proposal met the requirements of the RFP which covered previous experience, systems integration, capabilities and understanding of these types of applications. HSQ's many years of experience, coupled with our MISER software and hardware products, allowed us to propose a system that would meet and exceed the WTC requirements.
The HSQ model 2500/86 Logic Processor is used to monitor base building alarms and Chiller performance monitoring instruments. The system is designed to support future plans for energy management.
Project Scope
HSQ Technology was awarded the OCC/BMS design/build project, and the contract was signed in September of 1996. HSQ's proposal was based on HSQ's MISER software and Model 2500/86 Logic Processor RTUs. MISER will provide a central monitoring, control and information access facility for the following subsystems:
Elevator Monitoring and Control Escalator Monitoring Electrical Power Substation Monitoring and Control Base Building Alarm System Chiller Performance Monitoring System and HVAC Energy Management System Communication System Interface to a Work Order Management Software Package Interface to Existing Mainframe
Project Implementation
The delivered system consists of two main SCADA servers, 16 workstations, two system consoles, four printers, two terminal servers, Ethernet repeaters, hubs and associated LAN hardware, modems, facsimiles, and audio/visual equipment distributed throughout the different rooms. Communications between the different systems is via a fiber-based Campus Area Network (CAN). Originally, the CAN communications network was not part of this contract. However, the Port Authority has expanded the scope of the project to include the CAN System to be installed by HSQ. HSQ provided a 100 Mbps fiber optic ring multiplexor and Ethernet communications.
The Operations Control Center
The OCC (Operations Control Center) serves the following functions:
Operations Control
Performs day-to-day and emergency operations.
Emergency Operations
Functions as the communications center.
Tenant Liaison
Manages communications during emergencies.
The MISER SCADA system will interface to the elevator control and monitoring system. The WTC complex has 240 elevators and 48 Elevator Machine/Control Rooms. The Port Authority is in the process of upgrading the elevator controls. In the first stage, MISER will interface to 35 elevators. Other elevators will be added to the MISER system as they are upgraded. These controls include car leveling, door timing, floor bypass and emergency operation.
HSQ's SCADA system also monitors all 71 escalators distributed throughout the complex. The SCADA system monitors the operational state of the escalator (running or not running), direction of travel, and the presence of one of eight alarms. No control functions are envisioned at this time.
The WTC complex is served by an electrical distribution system consisting of 23 substations. Of these, 16 substations are located in the towers, each tower having 8 substations. Six of these have been upgraded to include digital devices such as power meters and digital protective relays. HSQ's MISER SCADA collects, processes and stores digital/analog data from the power meters, protective relays and other field devices. MISER utilizes the CAN System to communicate with these devices using SEAbus protocol. In the future, all substations will be upgraded and MISER will be communicating with all 23 substations.
The installed MISER system interfaces to approximately 385 alarm sensors strategically located throughout the building. The interface to the MISER system is through HSQ 2500/86 Remote Terminal Units (RTUs) that gather all the sensor data and transfer it to the main control center by means of the existing shielded twisted pair and via the fiber optic backbone network. The HSQ RTUs are designed to easily increase the number of alarm points that can display as the future need increases, and also to provide an interface for future energy management and control functions.
All alarms display at the individual Operator workstations. Alarms are color-coded and blink accordingly. By looking at the screen, an operator can easily identify the type of alarm, date and time that the alarm occurred, and which device caused the alarm. Alarms can be identified by priority or group, allowing the operator to easily identify alarms which have a high priority, markedly simplifying the operator's job. The User can build alarm displays for specific building functions or physical areas, or modify existing ones. MISER also provides advanced alarm processing functions such as historical archiving and reporting. Current alarms and historical alarm data can be printed or exported to other commercially available standard software packages for further analysis.
Since awarding the contract to HSQ, the Port Authority has expanded the scope of the project to include the Chiller Performance Monitoring System. In addition, there are plans to interface the HVAC Control System with HSQ's MISER system in the future. [end snip]
It wouldn't be surprising if there was a Y2k problem lurking somewhere in all this mess would it?
--- Harlan
Date: 08-May-98 17:43:03 MsgID: MC2-3C6E-C3B5 ToID: 71530,1637 From: Alan Reiss >INTERNET:AReiss.XOUT@PANYNJ.GOV Subj: Year 2000 - World Trade Center Elevators
Form: Memo Text: (40 lines follow) Dear Mr. Harlan Smith:
I was recently given a copy of what looks like a CompuServe forum message dated 3/24/98, # 10449 concerning y2k tests on the main elevators here. I do not what forum you attended where this information was presented but it is completely false. I was the supervising engineer for the World Trade up until the terrorist bombing, at which I took on the task of project director managing the reconstruction of the subgrade & infrastructure, then took over as the manager of the Capital programs for the World Trade Center. I selected the elevator modernization contractor & the controls currently being installed.
The original elevators at the WTC installed by Otis used relay logic controls with some transistor & Diode - Transistor Logic. This stuff was installed in the late 60's. It is really remarkable how well things work with "ancient technology". These units used tork time clocks to shift operation based on the time of day with cams.
In 1994 we began modernizing the 246 elevators at the WTC with microprocessor controls made by Computerized Elevator Controls. It is a non
proprietary system. The system is called Swift Futura. To date only 7 of the 46 "main" cars are modernized. They do not have a date function, though we are preparing to run and certify Y2K compliance tests with our contractor &
consultant this year. The vendor has already told us they are complaint but
we are from Missouri.
There was no test, elevator recall, shutdown etc. We may elevator problems due to the sway of a 110 story building and what it does to elevators but we sure don't have the Y2K problem you mentioned.
We are in fact lucky that we are just modernizing systems such as fire alarms and elevators rather than having done it in the 80's and then put a system that has a problem. For example most of the HVAC controls are still pneumatic. they don't care what the calendar sys.
Alan Reiss General Manager WTC Operations, Life Safety & Security
Use Proportional Font: true
**Primary Recipient: [71530,1637]
**CCs to: Theodore Stam INTERNET:TStam.XOUT@PANYNJ.GOV
But, after all this, there are still questions remaining. Where did John Bace, Director of Research at Gartner Group report that tale and where did he get that information? Before this is put fully to bed, I think we need an input from John Bace.
Harlan ___ Subject: Re: Electric Utilities vs Fear Mongers Date: 16 May 1998 02:25:17 EDT From: "Harlan Smith" <hwsmith.nowhere@cris.com> Organization: Paperless Newsgroups: comp.software.year-2000 References: 1 , 2 |